Transient Testing
Transient Test 1
Loaded/Unloaded
12v/5v
Test #1 is equal to approximately 25% of the rated capacity of the SilverStone NJ600 at 45c. This makes Test #1 equal to 149W by loading the 12v rail to 10a, the 5v rail to 2a, the 3.3v rail to 1a, the +5vsb to 2a, and the -12v to 0.3a before the addition of the transient load. The results of Test #1 show a ~340mV drop on the 12v rail and ~40mV drop on the 5v rail when each is directly loaded. At the same time that the load was being triggered on the 12v rail, the 5v rail measured a ~35mV drop.
Transient Test 2
Loaded/Unloaded
12v/5v
Test #2 is equal to approximately 50% of the rated capacity of the SilverStone NJ600 at 45c. This makes Test #2 equal to 301W by loading the 12v rail to 21a, the 5v rail to 4a, the 3.3v rail to 3a, the +5vsb to 2a, and the -12v to 0.3a before the addition of the transient load. The results of Test #2 show a ~320mV drop on the 12v rail and ~35mV drop on the 5v rail when each is directly loaded. At the same time that the load was being triggered on the 12v rail, the 5v rail measured a ~30mV drop.
The Transient Load Tests results for the SilverStone NJ600 are very good to excellent in an absolute sense. In today’s testing, the absolute values posted by the NJ600 saw the loaded 12v rail with a peak change of ~340mV and the loaded 5v rail with a peak change of ~40mV. The unloaded 5v peak change during the 12v load was ~35mV. These results
would be easily competitive to top of its class in a relative sense as well. So, the NJ600 is certainly doing things right in this regard in a relative and absolute sense today. Let’s move on now to see how this unit does in the DC Output Quality aspect of our testing!