Mild OC Testing
For our Mild OC testing, we have configured our CPU to run 4300MHz on all cores, set the voltage to 1.15V, and configured memory to XMP mode. This yields an approximate power at the wall of 450w under load (a 350w differential from idle, which pulls about 100w). This results in the CPU running at 4.3GHz on all cores during the looping rounds of Cinebench R20. You can read more about this in our introduction article here.
Max Fans – 100% Pump Speed
Running our AIO at full tilt on fans and pumps lead to a tie score with the LIQTECH II 360mm and H115i Platinum both hitting 73 degrees Celsius. A bit surprisingly though, the PF360-RGB posted a temperature of just 71 degrees Celsius. The max fan speed on the LIQTECH was 2250 RPM, the PF360-RGB was 2000 RPM, and the H115i was 1800 RPM.
Bringing the fans down to 1500 RPM boosted the SilverStone PF360-RGB temperatures by 4 degrees to 75 degrees Celsius, but the Corsair H115i only gave up one degree with a temperature of 74 degrees Celsius reported.
With the fans set to 1000 RPM, the SilverStone PF360-RGB was able to sustain 82 degrees Celsius under load. That is a full two degrees cooler than the Corsair H115i Platinum which was at 84 degrees Celsius.
600 RPM Fans – 50% and 100% Pump Speed
At the 600 RPM fan speed at both 50% and 100% pump speeds, all of the units let the temperature get out of control and thermal throttling kicked in as the CPU temperature reached above 98 degrees Celsius.